300 gallon System on the same breaker as da fridge.......?

GreatWhiteShart

New Member
View Badges
Joined
Oct 31, 2021
Messages
10
Reaction score
5
Location
Sarasota
What state or country do you live in
Florida
Rating - 0%
0   0   0
Should I attempt this.........
Or run a new breaker....
Equipment
Dcp 20000 jebao return
Rsk 600 skimmer
2x photon v2+
2x aquatic life 4 bulb t5 hybrids
Heater
And mars hydro 195w grow light

Am I asking doe trouble?

J
 
Depends what amps your breaker is.
Add up the amps of all the gear and fridge, assume all are 100% power, and if that is less than the amps on the breaker, your golden.... until someone plugs in the vacuum!
 
Last edited:
Watts divided by volts gives you amps.
Like 30 watt pump divided by 120 volts from the outlet equals .25 amps
 
I'd run two separate circuits and divide your flow across them with at least the return on with powerheads on another so that a single breaker tripping doesn't kill the tank. It's a small cost increase over running one, especially compared to the cost of what's going to be in the tank.
 
I would at least run a new 20 amp circuit for the 300 gallon. The problem with fridges is when the compressor first kicks on, you might over amp the circuit, shutting off power to the tank.
Depends what amps your breaker is.
Add up the amps of all the gear and fridge, assume all are 100% power, and if that is less than the amps on the breaker, your golden.... until someone plugs in the vacuum!
For continuous load, you need to be at 80% or less of the amperage on the breaker. So a 20 amp breaker should have no more than 16 amps continuously.
 
dont know about your place but my house is less than 10 old and the refrigerators are not on dedicated circuits...the 20 amp circuit ran to the fridge first, then to a gfi outlet with the additional kitchen outlets downstream of the gfi...cheap and stupid...my house is a modular so maybe their codes are different....your fridge outlet wouldnt be a gfi as compressors can trip them...give your tank its own dedicated circuits...if something goes horribly wrong you dont need a tank full of dead fish and a fridge full of spoiled food
 
dont know about your place but my house is less than 10 old and the refrigerators are not on dedicated circuits...the 20 amp circuit ran to the fridge first, then to a gfi outlet with the additional kitchen outlets downstream of the gfi...cheap and stupid...my house is a modular so maybe their codes are different....your fridge outlet wouldnt be a gfi as compressors can trip them...give your tank its own dedicated circuits...if something goes horribly wrong you dont need a tank full of dead fish and a fridge full of spoiled food

In the US under NEC code there is no requirement for a refrigerator to be on its own circuit and no requirement that it be a 20amp circuit. It is a best practice to have it on its own circuit, but when you talking about modular homes often saving a few dollars to the builder causes best practices to be thrown out the window.
 
thats for sure...in a 3000 sq ft house all 3 bathrooms run off one gfi outlet...meanwhile the microwave gets its own circuit...
 
Last edited:
Code here is dedicated breaker for Fridge and separate for Microwave.

I'd say run at least 2 separate new breakers for 300 Gallon setup.
In the US under NEC code there is no requirement for a refrigerator to be on its own circuit and no requirement that it be a 20amp circuit. It is a best practice to have it on its own circuit, but when you talking about modular homes often saving a few dollars to the builder causes best practices to be thrown out the window.

Strange and I quote.

The National Electrical Code (NEC) requires a dedicated circuit for any major electrical appliances in a home, such as washers, dryers, refrigerators, and dishwashers. The NEC calls it an “individual branch circuit,” although it means the same thing.
 
Code here is dedicated breaker for Fridge and separate for Microwave.

I'd say run at least 2 separate new breakers for 300 Gallon setup.


Strange and I quote.

The National Electrical Code (NEC) requires a dedicated circuit for any major electrical appliances in a home, such as washers, dryers, refrigerators, and dishwashers. The NEC calls it an “individual branch circuit,” although it means the same thing.

Nothing strange about it....and i quote...."Although it's an accepted standard for homes to have a separate circuit in the panel for the fridge, the NEC does allow a refrigerator to be connected to one of the two required 20-amp kitchen counter receptacle circuits [NEC 210.52(B)(1)]. We hardly ever see it done, but it is allowed. And no other permanently installed kitchen appliances, like disposals or dishwashers, are granted this exception per NEC."


I will admit there is some confusion on it because it is more than just looking at the codes but also NEC clarification and exceptions and more confusing when you add in the various versions of the NEC as jurisdictions may enforce different versions.
 
The NEC is correct about having your own branch circuit.
Large appliances like these tend to be power hungry and relatively noisy to boot in regards to electrical interference. Even if they don't produce a back feed that is potentially noisy, the drop in power a refrigerator produces during the starting phase of the compressor could potentially harm sensitive electronics.

With the price and sensitivity of the equipment you plan on using, the cost of having a professional run a dedicated GFCI circuit will seem cheap. EDIT: A dedicated line for the fish tank.
 
You guys really do geek da **** out I love it, im just going to run 2 circuits 2 20amps, one for sump, the other for circulation heating. Not going to lie its like a 10 foot run to my pannel....... and a day of dry wall no biggie
 
You guys really do geek da **** out I love it, im just going to run 2 circuits 2 20amps, one for sump, the other for circulation heating. Not going to lie its like a 10 foot run to my pannel....... and a day of dry wall no biggie
Yes 2 dedicated 20 amp circuits for a 300 gallon system. I like to split it up on mine I have 2 pumps and 2 heaters one on each circuit for redundancy
 
Nothing strange about it....and i quote...."Although it's an accepted standard for homes to have a separate circuit in the panel for the fridge, the NEC does allow a refrigerator to be connected to one of the two required 20-amp kitchen counter receptacle circuits [NEC 210.52(B)(1)]. We hardly ever see it done, but it is allowed. And no other permanently installed kitchen appliances, like disposals or dishwashers, are granted this exception per NEC."


I will admit there is some confusion on it because it is more than just looking at the codes but also NEC clarification and exceptions and more confusing when you add in the various versions of the NEC as jurisdictions may enforce different versions.
Talon is largely correct here. The US NEC is essentially now the same as CEC. As per below. ...

'15. Refrigerators

2015 Code — separate circuit required for each receptacle installed for a refrigerator

2018 Code — separate circuit only required for mandated refrigerator receptacle

The existing wording of 26-722 required a separate circuit for each receptacle installed for a refrigerator. This requirement is now relaxed by permitting a dedicated circuit to supply more than one refrigerator receptacle. It has also been revised to more clearly state that the requirement only applies to receptacles mandated by 26-712(d)(i) for refrigerators in kitchens. The requirement does not apply to refrigerators installed in other locations '

As with all CEC and NEC wording on all rules they are up to interpretation by your local inspector. THIS is key.

Licenced Journeyman CommercialElectrician of 25 years going for my Masters on Friday... so wish me luck. ;)

Oh, so ya, just install the separate circuit 20 amp here.
 