Again - there is no need to buy new controllers every year (if you buy quality) and you would be better served with TWO properly sized (~50% capacity) heaters and running your controllers in parallel. You remove the single point failure and rapid overheat protection. Want super safe and super redundant, then 2 controllers and 4 1/4 sized heaters. Or 3 controllers and 3 1/3 sized heaters, etc.
What is a quality controller? Example, A RANCO ETC controller has a power relay with a rated mechanical life of 1x10^7 cycles (full load) and an electrical rated life of 1x10^5 (full load)
In the case of a RANCO ETC - the full (120V) load rating is 16A - so 1920 Watts. If you are running a 1500W heater, that is 78% of the rated load. However, any SANE person would split that into two 750W or three 500W heaters for real world redundancy reasons. Seeing that you already have two controllers, then running them in parallel makes FAR more sense for both up-time and fail-safe as well as being gentle on their associated controllers.
We can argue about the difference between electrical and mechanical failure and which comes first... but unless you are hammering the relay with short cycles (sends or tenths of a second apart) mechanical failure is not going to happen. Likewise if you are running a load that is some percentage less than the rated output, then the electrical life is extremely unlikely to be met either. Also note that these numbers are Not MTBF numbers and rather minimum expected operating life, most (even at full load) will last many many times longer.
Any way you slice this - your "way" simply makes little sense if true redundancy or fail-safe operation are actually considered against real world probability.