Apex atk if command with time

Mr. GoodStuff

Active Member
View Badges
Joined
Mar 7, 2019
Messages
213
Reaction score
47
Location
60455
What state or country do you live in
Illinois
Rating - 0%
0   0   0
Fallback OFF
Set OFF
If ATK_LO OPEN Then ON
If ATK_HI CLOSED Then OFF
If ATO_LO OPEN Then OFF
When On > 001:30 Then OFF
Defer 000:20 Then ON
Defer 000:10 Then OFF
Min Time 060:00 Then OFF

So that’s my current ATK lines. Is it possible to set the ATK_HI portion with time? So it only activates that line after a set amount of time, like if ATK_HI is CLOSED for more than 10 seconds then it will turn OFF instead of immediately?

If ATK_HI CLOSED > 000:020 Then OFF

Is that a thing? My issue is the optical sensors are right below the float valve so when it fills the water basically runs down onto the optical sensors and sometimes triggers the ATK_HI sensor. If not possible I guess I can probably readjust some things.
 
You can take the ATK_HI and create a virtual outlet, then use the virtual outlet in this programing.
 
Last edited:
You can take the ATK_HI and create a virtual outlet, then use the virtual outlet in this programing.

but what 60 Min time. So its going to run for 60 minutes once tripped regardless.
Yea I ended up moving the float valve a little bit so it doesn’t dump water right on top of the sensor.
 