If you turn your return pumps down or off during feeding then the water level in the sump will be high and the ato won't come on anyways, No need to tell it to stay off. The sensors should be in the return section of the sump.
Here is my ato code using apex ato
Fallback OFF
Set OFF
If Sump_L OPEN Then ON (low optical sensor)
If Sump_H CLOSED Then OFF (high optical sensor)
If Res_Lo OPEN Then OFF (3rd optical sensor in ato resivior optional)
Defer 000:30 Then ON (low sensor has to be dry for 30 seconds to turn on)
Defer 000:15 Then OFF (low sensor has to be wet 15 seconds to turn off)
When On > 005:00 Then OFF ( this should never happen, it only takes about 1:30-2:00 minutes for mine to top off)
Min Time 030:00 Then OFF (waits 30 minutes before it will try to top off again)