I would love some help with this: I want my chiller to turn on if the tempature is above 79, but off when the tempature is below 78.5
At the same time, I want my apex to turn off my UV sterilizer and heaters when it is running. Thanks in advance!

#reefsquad
#apexusers
 
Last edited by a moderator:
I would love some help with this: I want my chiller to turn on if the tempature is above 79, but off when the tempature is below 78.5
At the same time, I want my apex to turn off my UV sterilizer and heaters when it is running. Thanks in advance!

#reefsquad
#apexusers

You'll need to update the code section on your chiller, UV, and heaters:

Chiller:
If Temp > 79.0 Then On
If Temp < 78.5 Then Off

UV:
(leave existing On/Off code in place)
If Output Chiller = On Then Off

Heater:
(leave existing On/Off code in place)
If Output Chiller = On Then Off

Be sure to use the actual input/output names for your temperature probe, chiller, UV, and heater in your code.
 