Hi,
I have an electrical question. Ive got a 100 gallon reef aquarium that requires two 12 outlet power strips. One of the strips uses all 12 outlets while the other uses 6 of the outlets. Both were plugged into the same wall outlet. Well, today, I noticed that the circuit breaker tripped and everything was off in the aquarium. Luckily I was home and was able to reset the breaker so the tank was only off for 30 minutes or so. The only thing ive changed is I moved one power strip plug from one outlet to another outlet but both are part of the same curcuit breaker so im not even sure that changes anything.

Just curious if anyone else has had this issue and what they did to resolve this. Just call an electrician? Im worried this will happen again when no one is home. Ive had the tank running for about 8 months and its the first time this has happened...
 
A few things can make a breaker trip,
#1 pulling to many amps your breakers are probably 15 amp
#2 maybe something id going to ground, do you have a meter?
#3 Heat can also make you draw more power in your breaker box hot?
You maybe have to separate your power out to a different breaker, I have not ever had this happen with todays new pumps and LED's but back in the day it happed a lot when I was using huge amount of power
 
Im in southern california and it was 115 outside (record heat) so the breaker box was probably really hot.
 
Im in southern california and it was 115 outside (record heat) so the breaker box was probably really hot.
This will cause you to pull more amps, in the plant I used to run I had to air-condition my power rooms but talking big power 10000 am panels
 
I ran a dedicated 20 amp circuit to my 70 G system. In your case I would first attempt to eliminate any non-aquarium loads from that circuit, i.,e, no vacuum cleaners. Also, are you able to split the aquarium load between two separate circuits?
 
I ran a dedicated 20 amp circuit to my 70 G system. In your case I would first attempt to eliminate any non-aquarium loads from that circuit, i.,e, no vacuum cleaners. Also, are you able to split the aquarium load between two separate circuits?

Unfortunately all the nearby plugs are part of the same circuit. Initially when this happened, I ran a long extension cord from another outlet from another circuit while I was figuring out what was going on. I might have to do this when I go on vacation....I have a tank of live rock with a heater and pump so I will move those somewhere else and move some other non vital stuff to a different circuit, thanks for all the suggestions so far.
 
So, I'm probably gonna have an electrician come in and install a new dedicated circuit, says it will cost around 300. I'm also thinking of getting a battery backup like an APC UPS 1500V. Do most people with battery backup attach a wavemaker pump or the return pump. The return pump will obviously use up more power. I've had a couple of power outages at my home last 4 years but none more than an hour or so....
 
Last edited:
You're on a single 15amp circuit leading back to your breaker box.

You're drawing more than 15amps.....Thank God the 15amp breaker did its job keeping house from burning down!

Easiest thing is to hire an electrician to swap out the 15amp to a 20amp breaker INSIDE the breaker box

Hth
 
Last edited:
You're on a single 15amp circuit leading back to your breaker box.

You're drawing more than 15amps.....do the 15amp breaker did it job keeping house from burning down!

Easiest thing is to hire an electrician to swap out the 15amp to a 20amp or higher breaker INSIDE the breaker box

Hth

Any idea how much that typically costs to do? I will ask about both options.
 
Note on 1500v UPS..

1500v is only going to give you less than 10mins of power when you throw in a "return pump" in the mix

Return pumps draw quite a few amps.

The more amps you draw....the quicker the UPS will drain.

Even the most massive UPSs out there only give you minutes of power bc reef equip all draw quite a few amps

When it comes to electricity..... volts mean very little..... it's the AMPERAGE values you have to take serious note of.

Hth
 
You're on a single 15amp circuit leading back to your breaker box.

You're drawing more than 15amps.....Thank God the 15amp breaker did its job keeping house from burning down!

Easiest thing is to hire an electrician to swap out the 15amp to a 20amp breaker INSIDE the breaker box

Hth

You can only do that if the wire is correct for a 20 amp circuit, most likely it will not be.
 
You can only do that if the wire is correct for a 20 amp circuit, most likely it will not be.
Correct. The breaker protects the wire. 14ga wire can safely carry a 15 amp load. 12ga wire can safely carry 20 amps. In theory, if you put a 20 amp breaker on a circuit wired with 14ga wire and something causes that circuit to carry more than 15amps, the wire would overheat and potentially start a fire before the 20 amp breaker would trip. Always smatch the size of the breaker to the size of the wire.

You did not say what size breaker you have now, is it 15 amps?

Technically you can undersize the breaker, using a 15 amp breaker on a 12ga circuit, and be ok because the breaker will always trip before you reach carrying capacity of the wire, but there is no real benefit to doing this.
That is why it is unlikely that you can safely replace your 15amp breaker with a 20 amp breaker - most likely the breaker was matched to the wire size. Easy enough to check though, just read the label on the wire connected to the breaker.
 
A couple more points:

- How old is the house? As breakers age, they trip more and more easily (I think that is by design), so simply replacing the breaker with a new one might help.

- If you pay $300 to have an electrician run a new circuit, run two. The labor is all the cost, he can wire each plug of a two socket outlet separately or do two outlets. Then each could be 20 amp, better to have it and not need it, then need it and not have it.

- Careful with a UPS, if you are not using it for a computer, you need to buy one with "sine wave output" or it can cause problems with some devices, like anything with a timer, and can damage some other equipment. The power supply in a computer compensates for that. And yes, you will get like 15 minutes, get one with a network card in it so that it can send you an alert when power is out.

I think the aquarium is probably using up most of your 15 amps, and you (or someone in your house) plugged something in to another outlet on the branch that put you over.

-JCL
 
Thanks for the advice everyone, Im thinking of maybe hooking up one of my wave pumps to the APC instead of the return pump, any idea about how long a wavepump can keep coral/fish alive in a 100 gallon reef without the function of the sump?
 
Last edited:
Just an update for anyone who runs into the same situation. I had the electrician install a dedicated 20 amp circuit. It ended up costing 495 due to the way my electrical circuits were layed out. I also got an APC 1500v that I have a wavepump hooked up to in case of a blackout, looks like it will run 4.5 hours on the battery. Hopefully this expensive detour will solve any electrical issues....
 
I'm not an electrician but ran into a similar issue with my 3 year old home also in California (I'm up North). If you do decide to call a electrician ask them to place a meter on the circuit in question to see what you are actually drawing. The reason why I say this is that I kept tripping the outlets in my den which houses our tank and thought I was drawing too much. I moved plugs and even ran extension cords to other rooms to power it. Same thing. Trip, trip, and trip again. Thus calling Elvis...er, I mean an Electrician :)

New home. New building codes. New so called smart breakers. Electrician told me how they get a lot of complaints about these things from users with high end stereo equipment and homes that run aquariums. Something to do with the sudden surge of demand from a 500 W heater for example or wave makers changing flow or ramping up. The breakers interrupt it has a failure trip. You go reset it, trips again. It may last for a couple hours then all of a sudden trips again because of the heather or other sudden draw. We replaced the breaker with another 15 amp but without said electronics built in and never seen the issue again.

Not saying that is your issue but when he came out the first thing he did was look at the den/office to see visually what sort of draw he might see. Then used a monitor, then said ok - here is the deal. Main thing is to really understand what you are using then go from there. The Electrician visit for me was actually free although he spent about an hour at the house. He couldn't see charging me for anything since he didn't really chase sparks/wire or do anything other than talk. Meter check was just being sure he said - I was pretty excited so wrote the company a personal letter so say thanks and how much of a great job they did.
 