HI, been going round and round trying to figure this out. Please chime in on what I need to do, thank you.
Yes, I have read the beginner article on Apex ATK.
The optical sensors are working fine and the PMUP is working fine.
ATK has been running a couple days now. It is constantly turning on and off... From my reading, it could be the float on the ATK in the turbulent sump...so I have tried various tweaks to no avail.
At the moment, the high water optical sensor is underwater/closed, but the ATK is still turning on and off. (When the high water optical sensor is open, the ATK turns on and off, too.) I see that the FMM on the EB8 is off when this happens as well. My concern is not only with the annoying noise of topoff bursts, but concern that the RODI pressure is at 0 for these bursts, thus the unit is not cleaning the water properly. The RODI system delivers water to a ATO 30 gal reservoir via float valve, the PMUP is located there and delivers water to the sump ATK.
Here is what I have in Fusion:
ATK PMUP Configuration -
Fallback OFF
Set OFF
If ATK_Lo OPEN Then ON
If ATK_Hi CLOSED Then OFF
If FW_lo OPEN Then OFF
When On > 003:00 Then OFF
Defer 003:10 Then ON
Defer 000:04 Then OFF
Min Time 060:00 Then OFF
FMM Configuration-
Fallback ON
Set ON
If ATK_Lo OPEN Then ON
If ATK_Hi CLOSED Then OFF
Defer 001:00 Then ON
Thank you.
Yes, I have read the beginner article on Apex ATK.
The optical sensors are working fine and the PMUP is working fine.
ATK has been running a couple days now. It is constantly turning on and off... From my reading, it could be the float on the ATK in the turbulent sump...so I have tried various tweaks to no avail.
At the moment, the high water optical sensor is underwater/closed, but the ATK is still turning on and off. (When the high water optical sensor is open, the ATK turns on and off, too.) I see that the FMM on the EB8 is off when this happens as well. My concern is not only with the annoying noise of topoff bursts, but concern that the RODI pressure is at 0 for these bursts, thus the unit is not cleaning the water properly. The RODI system delivers water to a ATO 30 gal reservoir via float valve, the PMUP is located there and delivers water to the sump ATK.
Here is what I have in Fusion:
ATK PMUP Configuration -
Fallback OFF
Set OFF
If ATK_Lo OPEN Then ON
If ATK_Hi CLOSED Then OFF
If FW_lo OPEN Then OFF
When On > 003:00 Then OFF
Defer 003:10 Then ON
Defer 000:04 Then OFF
Min Time 060:00 Then OFF
FMM Configuration-
Fallback ON
Set ON
If ATK_Lo OPEN Then ON
If ATK_Hi CLOSED Then OFF
Defer 001:00 Then ON
Thank you.