Why do we think the AC through the power bar is different than a power strip? The electronics in the thing are very low voltage (maybe 24 ma) and you will never get more amps through a house breaker than it is rated for. You can run a 3 hp motor easily on a 20 amp breaker................I think anyway ................not an expert. I do run a 1500 watt heater with a 12 gauge cord with no problem Maybe an electrical engineer can chime in.o_O
 
@Brew12 Does this make sense to you? I'm still trying to figure out how a 10 gauge extension cord in between 14 or 12 gauge home wiring and the eb832 would be needed? Intrigued by Neptunes advice here.
 
An appliance or air conditioner extension is perfect, cheap and safe to use
 
This doesn't make sense. Extension cords are sized by the required length of the extension and the total current draw. The EB832 has a 15A fuse, so assuming you are running the cord less than 20 feet a 14g cord should be good enough, and definitely a 12 gauge. Even if you decide to make it safe for 20A a 12g cord should be fine. Methinks Neptune is just giving CYA advice and defaulting to the largest size possible.
 
Old thread here... but sounds like there are some knowledgeable electrical folks around...

When using an apex with multiple 1 foot flat-head extension cables feeding into the apex EB8 to make things look pretty, am I ok plugging in 2-prong devices like a heater and small return pump into the 3-prong extension cords? The instructions specify NOT to... but this may be a safety precaution for older homes? Thx for any insights!
 
Old thread here... but sounds like there are some knowledgeable electrical folks around...

When using an apex with multiple 1 foot flat-head extension cables feeding into the apex EB8 to make things look pretty, am I ok plugging in 2-prong devices like a heater and small return pump into the 3-prong extension cords? The instructions specify NOT to... but this may be a safety precaution for older homes? Thx for any insights!
Are you sure you’re reading them correctly? The 3rd prong is a ground connector that is normally unused. If the device you’re plugging in only has a 2 prong plug than it doesn’t need a ground. Plugging a 2 prong cord into a 3 prong extension that’s plugged into your apex is no different than plugging the 2 prong device directly in to the 3 prong apex outlet.

I think what you are probably reading is advice not to plug a grounded, 3 prong plug into a 2 prong outlet using a cheater. This can leave the entire device ungrounded, a potential safety concern.
 
Are you sure you’re reading them correctly? The 3rd prong is a ground connector that is normally unused. If the device you’re plugging in only has a 2 prong plug than it doesn’t need a ground. Plugging a 2 prong cord into a 3 prong extension that’s plugged into your apex is no different than plugging the 2 prong device directly in to the 3 prong apex outlet.

I think what you are probably reading is advice not to plug a grounded, 3 prong plug into a 2 prong outlet using a cheater. This can leave the entire device ungrounded, a potential safety concern.
Yeah - misread in the wee-hours of reefing last night. Many thanks for the thorough response. Much appreciated.
 