A 300 watt heater on 120 volt power supply will only draw 2.5 amps....therefor a regular light household extension cord is fine
I have a similar question. I'm adding three frag tanks to my 300 gallon tank, which are all in my mancave. I was thinking of increasing the circuit breaker from 15 amps, since my room is already close to being maxed out.@Brad Miller, you are 100 percent correct. The issue I have is that I'm sure he only needs a couple feet of extension cord, and the issue I have is finding a short cord that has the grounding plug. That's the reason I recommend the appliance cords...they are all with the grounding plug and come in various short lengths. Find a 14 or 16 gauge wire cord that is short and with a ground and you're also good to go.
Are you sure that both circuits are exclusively used for that room? Many times there will be other areas the circuit will run to. I have one in my house that travels from the garage, to the front exterior of the house, to the basement, and then to the back exterior of the house. Just something to keep in mind when thinking about the load on the circuit.I have a similar question. I'm adding three frag tanks to my 300 gallon tank, which are all in my mancave. I was thinking of increasing the circuit breaker from 15 amps, since my room is already close to being maxed out.
However, I discovered my mancave has 2 breakers dedicated to it; so I want to split the power load between the two breakers by running an extension cord to the other side of the room. Now to my questions:
- Can I use an industrial grade power cord to permanently connect/extend my main power strip (American DJ) to the other breaker?
- Can I daisy chain multiple American DJ power strips together on a rack? This is how I've run my system for several years now.
Are you sure that both circuits are exclusively used for that room? Many times there will be other areas the circuit will run to. I have one in my house that travels from the garage, to the front exterior of the house, to the basement, and then to the back exterior of the house. Just something to keep in mind when thinking about the load on the circuit.
You can run an extension cord to the other side of the room but I would use at least 14 gauge grounded cord. That’s what a 15 amp circuit would have in the wall.
You had mentioned “increasing the circuit breaker from 15 amps”. I hope you’re not thinking of simply popping off the 15 amp one and sticking a 20 amp one in its place. You would also need to change the wiring from the panel to the outlet with 12 gauge wire and swap out the plug for a 20 amp plug too.
Thanks for the reply.Short answer is no. Why? Extension cords are not a replacement for fixed wiring. To me it sounds like this is going to be long term.
Can you - sure. If you have a properly sized extension cord but if it was my house, or anyone in it, the answer would be no.
Thanks for the reply.
I'm going to try and set-up independent racks so I'm not having to use the extension cord; but I wanted the option should my piping run anywhere close to where the rack would be.