I'm setting up a DIY ATO. I am using 4 BRS vertical float switches, 2 redundant high water switches and two redundant low level switches. I am connecting them to an APEX I/O breakout box.
The Apex manual says:
So, each switch can be installed in 4 ways:
1. Wire on the bottom, float up = open
2. Wire on the bottom, float up = closed
3. Wire on the top, float up = open
4. Wire on the top, float up = closed
What is the right installation for the low water and high water switches?
The Apex manual says:
"The reason the orientation is important is for failures. If/when a float switch fails, more likely than not it will fail in the open position (float sticks, wire breaks, contacts don’t close, etc). In addition, when you disconnect the BB from the Apex base unit, all switches go to their OPEN state. So keep this in mind when you layout your floats.
You want the OPEN condition to trigger stopping something, like a pump. You don’t want OPEN to trigger a pump starting or you will have a nasty surprise some day."
However, the BRS float switches allow you to change which position is "open" by removing the clip and switching the orientation of the float.You want the OPEN condition to trigger stopping something, like a pump. You don’t want OPEN to trigger a pump starting or you will have a nasty surprise some day."
So, each switch can be installed in 4 ways:
1. Wire on the bottom, float up = open
2. Wire on the bottom, float up = closed
3. Wire on the top, float up = open
4. Wire on the top, float up = closed
What is the right installation for the low water and high water switches?