Hey people, if I want to control a dosing pump to turn on through a plug bar socket if my ph falls below 7.8 and turn off the socket when the ph hits or goes above a set value (say 8 how would I programme this? I have posted this on the GHL Facebook page but no one has answered. Can anyone help me here. Thanks
 
I do not know but the easiest way would probably to set the pH controller to nominal value 7.9 and hysteresis to 0.2. controller mode - two position. Knit that to a socket (my example S64) with pHx increase. Now will that socket go on at 7.8 and stop at 8. Knit that socket to a physical pump (my example 24) through the function pump react to

1644352236947.png


If you want a higher shout of - as an example 8,1 - change nominal value to 7.95 and hysteresis to 0.3

There is more complicated way to do it - but I think this is the easiest

Sincerely Lasse
 
Upvote 0
I do not know but the easiest way would probably to set the pH controller to nominal value 7.9 and hysteresis to 0.2. controller mode - two position. Knit that to a socket (my example S64) with pHx increase. Now will that socket go on at 7.8 and stop at 8. Knit that socket to a physical pump (my example 24) through the function pump react to

1644352236947.png


If you want a higher shout of - as an example 8,1 - change nominal value to 7.95 and hysteresis to 0.3

There is more complicated way to do it - but I think this is the easiest

Sincerely Lasse
Oh right ok I was thinking it was going to be something to do with Programmable logic?
 
Upvote 0
I do not know but the easiest way would probably to set the pH controller to nominal value 7.9 and hysteresis to 0.2. controller mode - two position. Knit that to a socket (my example S64) with pHx increase. Now will that socket go on at 7.8 and stop at 8. Knit that socket to a physical pump (my example 24) through the function pump react to

1644352236947.png


If you want a higher shout of - as an example 8,1 - change nominal value to 7.95 and hysteresis to 0.3

There is more complicated way to do it - but I think this is the easiest

Sincerely Lasse
Also I won’t be using a GHL doser. I will be using a versa so just want the socket to turn on at 7.80 and turn off at 8
 
Upvote 0
If you want a shout off total independent of the hysteresis - you need to use virtual probes and PL. But this work and it is easy- The probe this way. I use my pH 1 as an example. And from GCC. My example S30 - you need to have the one you have to your doser

1644354102289.png





Sincerely Lasse
 
Upvote 0
If you want a shout off total independent of the hysteresis - you need to use virtual probes and PL. But this work and it is easy- The probe this way. I use my pH 1 as an example. And from GCC. My example S30 - you need to have the one you have to your doser

1644354102289.png





Sincerely Lasse
So what I am trying to do is to get a dosing pump (versa) to turn on when ph hits 7.8 and then switch off when it hits 8. This is to dose kalkwasser
 
Upvote 0
So what I am trying to do is to get a dosing pump (versa) to turn on when ph hits 7.8 and then switch off when it hits 8. This is to dose kalkwasser

And my example above does that

Sincerely Lasse
 
Upvote 0