I have a dedicated 20 AMP circuit, my plan was to run all my lights on this 1 Circuit. (12x LED Lights)
The Light is rated at 220W, but I've been monitoring one of them over the day on my profile, and it peaks at 157W.
12 X 157 = 1884, that's below the 80% of a 20 AMP circuit of 1920W, but it's a bit too close for comfort, and also, I'm not sure if there's a rule that says I need to factor in the full 220W of the Light fixture for safety reasons?