I plan on running a dedicated circuit for my tank but you can look into the circuit available at your tank's location and determine if its needed. I have a 225gal tank with LED lights and DC pumps. As displayed on Apex and confirmed at my breaker box using a induction DMM, during "normal" operation my tank only uses ~3amps. With the heater on that'll go to ~5amps. I put everything on 100% and it was ~10amps. If you have a 15amp circuit with minimal other loads (i.e. no refrigerator, TV, microwave, vacuum) I would propose a new circuit wouldn't be mandatory and you'd be relatively safe on it.
That said, in terms of safety measures, running a dedicated circuit would be a good idea. Running two as others suggest would be better, however maybe outside of what maybe practical. Seeing as many run Apex, you'd need two EB832's. Its hard to argue its a bad idea but like many best practices in this hobby, I would suggest the majority of reefers don't fully comply with it and most are just fine in doing so.