put an Apex solenoid on the line from your RO/DI to the sump. Then put an optical sensor in your sump at a high point. In the programming for your RO/DI solenoid, turn the solenoid off when the optical sensor is closed. Add a leak detector on the floor next to your sump for fail safe. Problem avoided. You could put the ATO in place in your sump and run your mixed salt directly in versus the RO/DI.
Here's the solenoid programming I have for my RO/DI into my mixing station
Fallback OFF
Set ON
If Mix_Lo CLOSED Then ON
If Time 00:00 to 13:00 Then OFF
If Time 13:01 to 23:59 Then ON
If Leak_F CLOSED Then OFF
If Leak_S CLOSED Then OFF
If LkMx_L CLOSED Then OFF
If LkMx_R CLOSED Then OFF
If Mix_Lv CLOSED Then OFF