If your voltage is anything less than 110 volts, don't worry about it. It is not from anything faulty. Any AC electrical device will induce voltage in anything near it. If you walk under a transformer over the street some voltage will be induced into your head. You know those guys with the purple Mohawks? They walked under a lot of transformers. GFCI's are not affected by induced voltage and you should not be either.
If the reading is 110 or higher, that comes from a short and when you stick your hand in the water, you will be thrown across the room so you will not need a multimeter to tell you there is a problem.
(Master electrician 40 years, retired)
If the reading is 110 or higher, that comes from a short and when you stick your hand in the water, you will be thrown across the room so you will not need a multimeter to tell you there is a problem.
(Master electrician 40 years, retired)





seeing that you use 240v and in india I'm assuming your supply is ac? i'm also assuming due to the relationship between uk and india that if you are using 240v ac the you would probably be using a similar type of earthing arrangement ...tt (terra terra old style)....or tncs (terra neutral combined separated) for your mains supply safety system? if so i wouldn't fit an earth (grounding) rod as you could then be mixing two different types of earthing system and probably going to create a problem with the (potential fault path) of your system. if you had an electrical fault with your system then you would want the designed fault path to do the work of protecting the system.