Feb 2, 2022 #1 Naturalreef Well-Known Member View Badges Joined Oct 3, 2015 Messages 805 Reaction score 638 Rating - 100% 3 0 0 Can someone please post their programming to silence Neptune Atk alarm when in feed mode please. Thank-you!
Can someone please post their programming to silence Neptune Atk alarm when in feed mode please. Thank-you!
Feb 2, 2022 #2 SuncrestReef That Apex guy View Badges Excellence Award Reef Tank 365 Article Contributor Reef Squad Emeritus Controller Advisor Joined Jan 18, 2018 Messages 4,214 Reaction score 9,251 Location Oregon Rating - 0% 0 0 0 The best way is to use a virtual output to monitor the ATK sensor and Feed mode, then only report on the virtual output in the actual alarm code: [Alarm_ATK_Hi] — new virtual output Set OFF If ATK_Hi CLOSED Then ON If FeedA 001 Then OFF [EmailAlm] Set OFF If Output Alarm_ATK_Hi = ON Then ON This method allows all of your other alarm conditions to still be monitored during Feed, with only the ATK excluded. If you’re not familiar with virtual outputs, see my tutorial here: Neptune Apex Programming Tutorials, Part 5: Virtual Outputs Part 5 of our Apex Programming Tutorials. This one is on Virtual Outputs. www.reef2reef.com
The best way is to use a virtual output to monitor the ATK sensor and Feed mode, then only report on the virtual output in the actual alarm code: [Alarm_ATK_Hi] — new virtual output Set OFF If ATK_Hi CLOSED Then ON If FeedA 001 Then OFF [EmailAlm] Set OFF If Output Alarm_ATK_Hi = ON Then ON This method allows all of your other alarm conditions to still be monitored during Feed, with only the ATK excluded. If you’re not familiar with virtual outputs, see my tutorial here: Neptune Apex Programming Tutorials, Part 5: Virtual Outputs Part 5 of our Apex Programming Tutorials. This one is on Virtual Outputs. www.reef2reef.com
Feb 2, 2022 #3 OP OP Naturalreef Well-Known Member View Badges Joined Oct 3, 2015 Messages 805 Reaction score 638 Rating - 100% 3 0 0 Thank you so much for posting that Sun!