You may have mentioned previously, what is your setup for your heater/ linked to apex? Read most people use a heater controller plugged into apex as a secondary measure. Need to pull the trigger on a heater for my reefer. Also running apex. TIA
I have a Finnex 300w titanium heater which does not have any built-in thermostat. I plug that into an Inkbird heater controller. The Inkbird is set to keep the tank between 77 - 80 degrees F. Then I have the Inkbird plugged into the Apex EB832, and it's set to turn on the heater if below 77.8 and turn it off if over 78.0:
Fallback OFF
If Tmp < 77.8 Then ON
If Tmp > 78.0 Then OFF
Defer 001:00 Then ON
Defer 000:15 Then OFF
So the Apex is the primary controller for the heater, but if for some reason it fails to turn off the heater when over 78.0, the Inkbird will override and turn off the heater if it reaches 80 degrees.
My reasoning for this configuration is that the Inkbird is terrible at keeping a tight temperature range. The best I could get from it was about a 1.1 degree range. The Apex can keep the tank within 0.1 degrees F, and I prefer to maintain a tight temperature range, so using the Apex as the primary and Inkbird as the failsafe gives me the control I want.
You'll hear many people argue that this will cause the EnergyBar output relay to wear out from too frequent On/Off transitions. However, the EB832 relays are rated for over 1 million cycles. Reviewing my output logs, I see that my heater turns on and off about 50 times per day on average. At this rate, that's 18,250 cycles per year, so it would take over 54 years to reach 1 million cycles. I've been running my heater and EB832 this way for over 3 years with no problem, and I don't lose any sleep over it.