Unplug lights, it all goes away.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Yup, looks like you have a fault in your lighting and a bad ground path. I've helped quite a few people who thought their lights were shocking them where it wasn't the case. I think you are the first person who actually has a bad light!Unplug lights, it all goes away.
Nice! Makes further troubleshooting easy. Odds of having identical faults in both lights is almost none. Looks like you have an open ground in your power strip and the corrosion is tracking from hot to the grounds of your lights. A new power strip should fix your situation if I'm guessing right.Here's the bracket setup..![]()
It could be an artifact from induced voltages with your DC pumps. Since they operate by creating a new AC voltage at a variable frequency the fault voltage from the lights could read a difference compared to the induced voltage from the DC pumps.I don't understand how the V is getting into the water.. must be salt creep somewhere. The bracket is isolated from the water.
![]()
Glad to help. Although I doubt you really needed it. Sometimes it just helps to talk things through.Brew, thank you for helping me think this through!
I checked again and the instructions for that meter are pretty clear that it doesn't measure current using the probes.That meter should read amps through the probes but you have to put it in line with the load.
Find anything today?Brew, thank you for helping me think this through!
I'm not an EE but I work as one. No college but did 10 years as a Navy nuke electrician. Now I handle all the projects and maintenance for a 500kV substation with 960MVA of installed main transformers along with my industrials entire power distribution system.@Brew12 you're awesome! Love when there are other people like me out there. I'm a EE. You too?
My first guess here is a missing case ground strap. You can check continuity between the case and the ground pin of the power cord for the light. I'm going to guess it is open on one of the lights.
Ah, a Navy nuke. Makes sense nowI'm not an EE but I work as one. No college but did 10 years as a Navy nuke electrician. Now I handle all the projects and maintenance for a 500kV substation with 960MVA of installed main transformers along with my industrials entire power distribution system.
I think this has to be a power strip issue. With 2 separate lights he would have to have a bad ground connection in each which I would consider unlikely. I'm guessing the ground connection in the power strip corroded and not only isn't connected to the home ground, but is using the light grounds to feed power to the case of the fixtures.
Would love verification!

It was a combination of these 2 comments combined with the picture of his system showing that his lights don't come close to making contact with his tank.Ah, a Navy nuke. Makes sense now
I must have missed a detail where you got that impression. It looked to me like the measurements were coming from the light rail to the ground and it looks to me like the lights are mounted with metal cables and caribiners. Carry on and I'll follow along too![]()
So, I got out my trusty fluke meter, and from ground to light bracket I get 32 volts AC.
The water voltage to ground drops to zero as well as the fixture to ground when the lights are unplugged.
Hmmm. Perhaps a combination of a bad ground in the power strip and a missing case ground is providing both the source and path. It could explain the 32vac source.It was a combination of these 2 comments combined with the picture of his system showing that his lights don't come close to making contact with his tank.
I think something is grounding out his tank and that the source of the 32VAC was his ground measuring point, not the tank.

Nice! I was a quitter... only did 10 years. Just didn't want to do another 5 years on a sub.@Brew12 - Thanks for your service. Fifteen years in USAF aerospace maintenance here.